All Topics  
Partial discharge

 

   Email Print
   Bookmark   Link






 

Partial discharge



 
 
In electrical engineering
Electrical engineering

Electrical engineering, sometimes referred to as electrical and electronic engineering, is a field of engineering that deals with the study and application of electricity, electronics and electromagnetism....
, a partial discharge (PD) is a localised dielectric breakdown of a small portion of a solid or liquid electrical insulation
Electrical insulation

An insulator, also called a dielectric, is a material that resists the flow of electric current. An insulating material has atoms with tightly bonded valence electrons....
 system under high voltage
High voltage

The term high voltage characterizes electrical circuits, in which the voltage used is the cause of particular safety concerns and insulation requirements....
 stress. While a corona discharge
Corona discharge

In electricity, a corona discharge is an electrical discharge brought on by the ionization of a fluid surrounding a conductor , which occurs when the potential gradient exceeds a certain value, but conditions are insufficient to cause complete electrical breakdown or electric arc....
 is usually revealed by a relatively steady glow or brush discharge in air, partial discharges within an insulation system may or may not exhibit visible discharges, and discharge events tend to be more sporadic in nature than corona discharges.

sually begins within voids, cracks, or inclusions within a solid dielectric, at conductor-dielectric interfaces within solid or liquid dielectrics, or in bubbles within liquid dielectric
Dielectric

A dielectric is a nonconducting substance, i.e. an Insulator . The term was coined by William Whewell in response to a request from Michael Faraday....
s.






Discussion
Ask a question about 'Partial discharge'
Start a new discussion about 'Partial discharge'
Answer questions from other users
Full Discussion Forum



Encyclopedia


In electrical engineering
Electrical engineering

Electrical engineering, sometimes referred to as electrical and electronic engineering, is a field of engineering that deals with the study and application of electricity, electronics and electromagnetism....
, a partial discharge (PD) is a localised dielectric breakdown of a small portion of a solid or liquid electrical insulation
Electrical insulation

An insulator, also called a dielectric, is a material that resists the flow of electric current. An insulating material has atoms with tightly bonded valence electrons....
 system under high voltage
High voltage

The term high voltage characterizes electrical circuits, in which the voltage used is the cause of particular safety concerns and insulation requirements....
 stress. While a corona discharge
Corona discharge

In electricity, a corona discharge is an electrical discharge brought on by the ionization of a fluid surrounding a conductor , which occurs when the potential gradient exceeds a certain value, but conditions are insufficient to cause complete electrical breakdown or electric arc....
 is usually revealed by a relatively steady glow or brush discharge in air, partial discharges within an insulation system may or may not exhibit visible discharges, and discharge events tend to be more sporadic in nature than corona discharges.

Discharge mechanism

PD usually begins within voids, cracks, or inclusions within a solid dielectric, at conductor-dielectric interfaces within solid or liquid dielectrics, or in bubbles within liquid dielectric
Dielectric

A dielectric is a nonconducting substance, i.e. an Insulator . The term was coined by William Whewell in response to a request from Michael Faraday....
s. Since discharges are limited to only a portion of the insulation, the discharges only partially bridge the distance between electrodes. PD can also occur along the boundary between different insulating materials.

Partial discharges within an insulating material are usually initiated within gas-filled voids within the dielectric. Because the dielectric constant
Dielectric constant

The relative static permittivity of a material under given conditions is a measure of the extent to which it concentrates electrostatic lines of flux....
 of the void is consideraby less than the surrounding dielectric, the electric field
Electric field

In physics, the space surrounding an electric charge or in the presence of a time-varying magnetic field has a property called an electric field ....
 (and the voltage
Voltage

Electrical tension is the potential difference between two points of an electrical or electronic circuit, expressed in volts. It is the measurement of the potential for an electric field to cause an electric current in an electrical conductor....
 stress) appearing across the void is significantly higher than across an equivalent distance of dielectric. If the voltage stress across the void is increased above the corona
Corona

A corona is a type of Plasma "celestial body's atmosphere" of the Sun or other celestial body, extending millions of kilometres into space, most easily seen during a total solar eclipse, but also observable in a coronagraph....
 inception voltage (CIV) for the gas within the void, then PD activity will start within the void.

Once begun, PD causes progressive deterioration of insulating materials, ultimately leading to electrical breakdown
Electrical breakdown

The term electrical breakdown has several similar but distinctly different meanings. The term can apply to the failure of an electrical network....
. PD can be prevented through careful design and material selection. In critical high voltage equipment, the integrity of the insulation is confirmed using PD detection equipment during the manufacturing stage as well as periodically through the equipment's useful life. PD prevention and detection are essential to ensure reliable, long-term operation of high voltage equipment used by electric power utilities
Electrical power industry

The electrical power industry provides the production and delivery of electrical power , often known as power, or electricity, in sufficient quantities to areas that need electricity through a grid connection....
.

Partial discharge equivalent circuit

The equivalent circuit of a dielectric incorporating a cavity can be modeled as a capacitive voltage divider in parallel with another capacitor. The upper capacitor of the divider represents the parallel combination of the capacitances in series with the void and the lower capacitor represents the capacitance of the void. The parallel capacitor represents the remaining unvoided capacitance of the sample.

Partial discharge currents

When partial discharge is initiated, high frequency transient current pulses will appear and persist for nano-seconds to a micro-second, then disappear and reappear repeatedly. PD currents are difficult to measure because of their small magnitude and short duration. The event may be detected as a very small change in the current drawn by the sample under test. One method of measuring these currents is to put a small current-measuring resistor
Resistor

|- align = "center"||width = "25"|| |- align = "center"||| Potentiometer|- align = "center"| || |- align = "top"| Resistor|| Variable resistor...
 in series with the sample and then view the generated voltage on an oscilloscope
Oscilloscope

An oscilloscope is a type of electronic test instrument that allows signal voltages to be viewed, usually as a two-dimensional graph of one or more electrical potential differences plotted as a function of time or of some other voltage ....
 via a matched coaxial
Coaxial

In geometry, coaxial means that two or more forms share a common Coordinate axis; it is the three-dimensional linear analog of "concentric".Coaxial cable, as a common example, has a wire Conductor in the center a circumferential outer conductor and an insulating medium called the dielectric separating these two conductors....
 cable.

Apparent Charge

The actual charge change that occurs due to a PD event is usually not directly measurable. Apparent charge is used instead. The apparent charge (q) of a PD event is not the actual amount of charge changing at the PD site. Instead, it is the change in charge that, if injected between the terminals of the device under test
Device under test

Device under test , also known as unit under test , is a term commonly used to refer to a manufactured product undergoing testing....
, would change the voltage across the terminals by an amount equivalent to the PD event. This can be modeled by the equation:

The apparent charge is not equal to the actual amount of changing charge at the PD site, but is more realistic than . 'Apparent charge' is usually expressed in picocoulomb
Coulomb

The coulomb is the SI unit of electric charge. It is named after Charles-Augustin de Coulomb....
s. partial discharge is not electronic.

Discharge detection and measuring systems

A number of discharge detection schemes have been invented since the importance of PD was realised early in the last century. Partial discharge currents tend to be of short duration and have rise times in the nanosecond regime. On an oscilloscope
Oscilloscope

An oscilloscope is a type of electronic test instrument that allows signal voltages to be viewed, usually as a two-dimensional graph of one or more electrical potential differences plotted as a function of time or of some other voltage ....
, the discharges look like randomly occurring 'spikes' or pulses. The usual way of quantifying partial discharge magnitude is in picocoulomb
Coulomb

The coulomb is the SI unit of electric charge. It is named after Charles-Augustin de Coulomb....
s.

Calibration setup
This is measured by calibrating the voltage of the spikes against the voltages obtained from a calibration unit discharged into the measuring instrument. The calibration unit is quite simple in operation and merely comprises a square wave generator in series with a capacitor connected across the sample. Usually these are triggered optically to enable calibration without entering a dangerous high no voltage area. Calibrators are usually left connected during the discharge testing.

Laboratory methods

Wideband PD detection circuits

In wideband
Wideband

In Telecommunication, wideband is a relative term used to describe a wide range of frequencies in a spectrum. A system is typically described as wideband if the message bandwidth significantly exceeds the channel's coherence bandwidth....
 detection
Detection

In general, detection is the extraction of information from any clear or clouded ambient or otherwise accessible stream of information without neither support from the sender nor synchronization to the sender....
, the coupling impedance usually comprises a low Q
Q factor

In physics and engineering the quality factor or Q factor is a dimensionless parameter that compares the time constant for decay of an oscillating physical system's amplitude to its oscillation Frequency....
 parallel-resonant RLC circuit
RLC circuit

An RLC circuit is an electrical circuit consisting of a resistor , an inductor , and a capacitor , connected in series or in parallel. This configuration forms a harmonic oscillator....
. This circuit tends to attenuate the exciting voltage (usually between 50 and 60 Hz
Hertz

The hertz is a measure of frequency per unit of time, or the number of list of cycles per second. It is the SI base unit of frequency in the International System of Units , and is used worldwide in both general-purpose and scientific contexts....
) and to amplify the voltage generated due to the discharges.

Tuned (narrow band) detection circuits

Differential discharge bridge methods

Acoustic and Ultrasonic methods

Field testing methods
Clearly the field testing of plant and equipment in service by the above method, although it has been done, is not very convenient. Therefore field testing for PD activity has taken on a slightly different role where accuracy of measurement is less important than basic indication of discharge activity. To this end, a number of specialised instruments have been developed by many companies around the world.

Effects of partial discharge in insulation systems

PD are localised ionisation within electrical insulation that are caused by a high electrical field. They occur in part of the insulation system and are limited in extent, so they do not immediately cause full insulation breakdown.

PD can occur in a gaseous, liquid or solid insulating medium. It is often initiated within gas voids enclosed in solid insulation, or in bubbles within a liquid insulating material, such as voids in an epoxy insulator, or gas bubbles dissolved within transformer oil.

As the gas within the void has a dielectric constant much less than the surrounding material, it experiences a significantly higher electric field. When this becomes high enough to cause electrical breakdown in the gas, a partial discharge occurs. PD can also occur along the surface of solid insulating materials if the surface tangential electric field is high enough to cause a breakdown along the insulator surface. This phenomenon commonly manifests itself on overhead line insulators, particularly on contaminated insulators during days of high humidity. Overhead line insulators use air as their insulation medium.

The effects of PD within high voltage
High voltage

The term high voltage characterizes electrical circuits, in which the voltage used is the cause of particular safety concerns and insulation requirements....
 cables and equipment can be very serious, ultimately leading to complete failure. The cumulative effect of partial discharges within solid dielectrics is the formation of numerous, branching partially conducting discharge channels, a process called treeing
Electrical treeing

Within the field of electrical engineering, treeing is an electrical pre-breakdown phenomenon. It is a damaging process due to partial discharges and progresses through the stressed dielectric insulation, whose path resembles the form of a tree....
. Repetitive discharge events cause irreversible mechanical and chemical deterioration of the insulating material. Damage is caused by the energy dissipated by high energy electrons or ions, ultraviolet light from the discharges, ozone attacking the void walls, and cracking as the chemical breakdown processes liberate gases at high pressure. The chemical transformation of the dielectric also tends to increase the electrical conductivity of the dielectric material surrounding the voids. This increases the electrical stress in the (thus far) unaffected gap region, accelerating the breakdown process. A number of inorganic dielectrics, including glass
Glass

Glass generally refers to a Hardness, brittle, transparency amorphous solid, such as that used for windows, many Glass Bottles, or eyewear, including, but not limited to, soda-lime glass, borosilicate glass, acrylic glass, sugar glass, Muscovite , or aluminium oxynitride....
, porcelain
Porcelain

Porcelain is a ceramic material made by heating raw materials, generally including clay in the form of kaolin, in a kiln to temperatures between and ....
, and mica
Mica

The mica group of sheet silicate minerals includes several closely related materials having highly perfect basal cleavage. All are monoclinic with a tendency towards pseudo-hexagonal crystals and are similar in chemical composition....
, are significantly more resistant to PD damage than organic and polymer
Polymer

A polymer is a large molecule composed of repeating structural units typically connected by covalent chemical bonds. While polymer in popular usage suggests plastic, the term actually refers to a large class of natural and synthetic materials with a variety of properties....
 dielectrics.

In paper-insulated high-voltage cables, partial discharges begin as small pinholes penetrating the paper windings that are adjacent to the electrical conductor or outer sheath. As PD activity progresses, the repetitive discharges eventually cause permanent chemical changes within the affected paper layers and impregnating dielectric fluid. Over time, partially conducting carbonized trees are formed. This places greater stress on the remaining insulation, leading to further growth of the damaged region, resistive heating along the tree, and further charring (sometimes called tracking). This eventually culminates in the complete dielectric failure of the cable and, typically, an electrical explosion
Explosion

An explosion is a sudden increase in volume and release of energy in an extreme manner, usually with the generation of high temperatures and the release of gases....
.

PD dissipate energy, generally in the form of heat, but sometimes in as sound and light as well, like the hissing and dim glowing from the overhead line insulators. Heat energy dissipation may cause thermal degradation of the insulation, although the level is generally low. For high voltage equipment, the integrity of the insulation can be confirmed by monitoring the PD activities that occur through the equipment's life. To ensure supply reliability and long-term operational sustainability, PD in high-voltage electrical equipment should be monitored closely with early warning signals for inspection and maintenance.

International Standards

  • IEC
    International Electrotechnical Commission

    The International Electrotechnical Commission is a Non-profit organization, non-governmental international standards organization that prepares and publishes International Standards for all electrical, electronic and related technologies ? collectively known as "electrotechnology"....
     60270:2000/BS EN 60270:2001 "High-Voltage Test Techniques - Partial Discharge Measurements"
  • IEEE 400-2001 "IEEE Guide for Field Testing and Evaluation of the Insulation of Shielded Power Cable Systems"
  • IEEE 1434-2000 "IEEE Trial-Use Guide to the Measurement of Partial Discharges in Rotating Machinery"


See also

  • Electrical treeing
    Electrical treeing

    Within the field of electrical engineering, treeing is an electrical pre-breakdown phenomenon. It is a damaging process due to partial discharges and progresses through the stressed dielectric insulation, whose path resembles the form of a tree....


External links


  • white paper
    White paper