Transient Recovery Voltage
|
| |
|
| |
A transient recovery voltage (or TRV) for high-voltage circuit breakers is the voltage that appears across the terminals after current interruption. It is a critical parameter for fault interruption by a high-voltage circuit breaker, its characteristics (amplitude, rate of rise) can lead either to a successful current interruption or to a failure (called reignition or restrike).
The TRV is dependent on the characteristics of the system connected on both terminals of the circuit-breaker, and on the type of fault that this circuit breaker has to interrupt (single, double or three-phase faults, grounded or ungrounded fault ..).
Characteristics of the system include:
The most severe TRV is applied on the first pole of a circuit-breaker that interrupts current (called the first-pole-to-clear in a three-phase system).

Discussion
Ask a question about 'Transient Recovery Voltage'
Start a new discussion about 'Transient Recovery Voltage'
Answer questions from other users
|
Encyclopedia
A transient recovery voltage (or TRV) for high-voltage circuit breakers is the voltage that appears across the terminals after current interruption. It is a critical parameter for fault interruption by a high-voltage circuit breaker, its characteristics (amplitude, rate of rise) can lead either to a successful current interruption or to a failure (called reignition or restrike).
The TRV is dependent on the characteristics of the system connected on both terminals of the circuit-breaker, and on the type of fault that this circuit breaker has to interrupt (single, double or three-phase faults, grounded or ungrounded fault ..).
Characteristics of the system include:
- type of neutral (effectively grounded, ungrounded, solidly grounded ..)
- type of load (capacitive, inductive, resistive)
- type of connection: cable connected, line connected..
The most severe TRV is applied on the first pole of a circuit-breaker that interrupts current (called the first-pole-to-clear in a three-phase system). The parameters of TRVs are defined in international standards such as IEC and IEEE (or ANSI).
Capacitive load Typical cases of capacitive loads are unloaded lines and capacitor banks.
Inductive circuit
Short-circuit condition A circuit breaker interrupts a short-circuit at current zero, at this instant the supply voltage is maximum and the recovery voltage tends to reach the supply voltage with a high frequency transient. The normalized value of the overshoot or amplitude factor is 1.4.
Out-of-phase condition