Fault (power engineering)
Encyclopedia
In an electric power system
Electric power system
An electric power system is a network of electrical components used to supply, transmit and use electric power. An example of an electric power system is the network that supplies a region's homes and industry with power - for sizable regions, this power system is known as the grid and can be...

, a fault is any abnormal flow of electric current
Electric current
Electric current is a flow of electric charge through a medium.This charge is typically carried by moving electrons in a conductor such as wire...

. For example, a short circuit
Short circuit
A short circuit in an electrical circuit that allows a current to travel along an unintended path, often where essentially no electrical impedance is encountered....

 is a fault in which current flow bypasses the normal load. An open-circuit fault occurs if a circuit is interrupted by some failure. In three-phase
Three-phase electric power
Three-phase electric power is a common method of alternating-current electric power generation, transmission, and distribution. It is a type of polyphase system and is the most common method used by grids worldwide to transfer power. It is also used to power large motors and other heavy loads...

 systems, a fault may involve one or more phases and ground, or may occur only between phases. In a "ground fault" or "earth fault", current flows into the earth. The prospective short circuit current of a fault can be calculated for power systems. In power systems, protective devices detect fault conditions and operate circuit breaker
Circuit breaker
A circuit breaker is an automatically operated electrical switch designed to protect an electrical circuit from damage caused by overload or short circuit. Its basic function is to detect a fault condition and, by interrupting continuity, to immediately discontinue electrical flow...

s and other devices to limit the loss of service due to a failure.

In a polyphase system
Polyphase system
A polyphase system is a means of distributing alternating current electrical power. Polyphase systems have three or more energized electrical conductors carrying alternating currents with a definite time offset between the voltage waves in each conductor. Polyphase systems are particularly useful...

, a fault may affect all phases equally which is a "symmetrical fault". If only some phases are affected, the resulting "asymmetrical fault" becomes more complicated to analyse due to the simplifying assumption of equal current magnitude in all phases being no longer applicable. The analysis of this type of fault is often simplified by using methods such as symmetrical components
Symmetrical components
In electrical engineering, the method of symmetrical components is used to simplify analysis of unbalanced three phase power systems under both normal and abnormal conditions.-Description:...

.

Transient fault

A transient fault is a fault that is no longer present if power is disconnected for a short time.

Many faults in overhead powerline
Overhead powerline
An overhead power line is an electric power transmission line suspended by towers or utility poles. Since most of the insulation is provided by air, overhead power lines are generally the lowest-cost method of transmission for large quantities of electric energy...

s are transient in nature. At the occurrence of a fault power system protection
Power system protection
Power system protection is a branch of electrical power engineering that deals with the protection of electrical power systems from faults through the isolation of faulted parts from the rest of the electrical network...

 operates to isolate area of the fault. A transient fault will then clear and the powerline can be returned to service. Typical examples of transient faults include:
  • momentary tree contact
  • bird or other animal contact
  • lightning strike
  • conductor clash

In electricity transmission and distribution
Electricity distribution
File:Electricity grid simple- North America.svg|thumb|380px|right|Simplified diagram of AC electricity distribution from generation stations to consumers...

 systems an automatic reclose function is commonly used on overhead lines to attempt to restore power in the event of a transient fault. This functionality is not as common on underground systems as faults there are typically of a persistent nature. Transient faults may still cause damage both at the site of the original fault or elsewhere in the network as fault current is generated.

Persistent fault

A persistent fault does not disappear when power is disconnected. Faults in underground power cable
Power cable
A power cable is an assembly of two or more electrical conductors, usually held together with an overall sheath. The assembly is used for transmission of electrical power...

s are often persistent. Underground power lines are not affected by trees or lightning
Lightning
Lightning is an atmospheric electrostatic discharge accompanied by thunder, which typically occurs during thunderstorms, and sometimes during volcanic eruptions or dust storms...

, so faults, when they occur, are probably due to damage. In such cases, if the line is reconnected, it is likely to be only damaged further.

Symmetric fault

A symmetric, symmetrical or balanced fault affects each of the three-phases equally. In transmission line faults, roughly 5% are symmetric. This is in contrast to an asymmetric fault, where the three phases are not affected equally. In practice, most faults in power systems are unbalanced. With this in mind, symmetric faults can be viewed as somewhat of an abstraction; however, as asymmetric faults are difficult to analyze, analysis of asymmetric faults is built up from a thorough understanding of symmetric faults.

Asymmetric fault

An asymmetric or unbalanced fault does not affect each of the three phases equally.

Common types of asymmetric faults, and their causes:
  • line-to-line - a short circuit
    Short circuit
    A short circuit in an electrical circuit that allows a current to travel along an unintended path, often where essentially no electrical impedance is encountered....

     between lines, caused by ionization
    Ionization
    Ionization is the process of converting an atom or molecule into an ion by adding or removing charged particles such as electrons or other ions. This is often confused with dissociation. A substance may dissociate without necessarily producing ions. As an example, the molecules of table sugar...

     of air, or when lines come into physical contact, for example due to a broken insulator
    Electrical insulation
    thumb|250px|[[Coaxial Cable]] with dielectric insulator supporting a central coreThis article refers to electrical insulation. For insulation of heat, see Thermal insulation...

    .
  • line-to-ground - a short circuit between one line and ground, very often caused by physical contact, for example due to lightning
    Lightning
    Lightning is an atmospheric electrostatic discharge accompanied by thunder, which typically occurs during thunderstorms, and sometimes during volcanic eruptions or dust storms...

     or other storm
    Storm
    A storm is any disturbed state of an astronomical body's atmosphere, especially affecting its surface, and strongly implying severe weather...

      damage
  • double line-to-ground - two lines come into contact with the ground (and each other), also commonly due to storm damage

Analysis

Symmetric faults can be analyzed via the same methods as any other phenomena in power systems, and in fact many software tools exist to accomplish this type of analysis automatically (see power flow study
Power flow study
In power engineering, the power flow study is an important tool involving numerical analysis applied to a power system. A power flow study usually uses simplified notation such as a one-line diagram and per-unit system, and focuses on various forms of AC power...

). However, there is another method which is as accurate and is usually more instructive.

First, some simplifying assumptions are made. It is assumed that all electrical generator
Electrical generator
In electricity generation, an electric generator is a device that converts mechanical energy to electrical energy. A generator forces electric charge to flow through an external electrical circuit. It is analogous to a water pump, which causes water to flow...

s in the system are in phase, and operating at the nominal voltage
Voltage
Voltage, otherwise known as electrical potential difference or electric tension is the difference in electric potential between two points — or the difference in electric potential energy per unit charge between two points...

 of the system. Electric motor
Electric motor
An electric motor converts electrical energy into mechanical energy.Most electric motors operate through the interaction of magnetic fields and current-carrying conductors to generate force...

s can also be considered to be generators, because when a fault occurs, they usually supply rather than draw power. The voltages and currents are then calculated for this base case.

Next, the location of the fault is considered to be supplied with a negative voltage source, equal to the voltage at that location in the base case, while all other sources are set to zero. This method makes use of the principle of superposition
Superposition principle
In physics and systems theory, the superposition principle , also known as superposition property, states that, for all linear systems, the net response at a given place and time caused by two or more stimuli is the sum of the responses which would have been caused by each stimulus individually...

.

To obtain a more accurate result, these calculations should be performed separately for three separate time ranges:
  • subtransient is first, and is associated with the largest currents
  • transient comes between subtransient and steady-state
  • steady-state occurs after all the transients have had time to settle


An asymmetric fault breaks the underlying assumptions used in three phase power, namely that the load is balanced on all three phases. Consequently, it is impossible to directly use tools such as the one-line diagram
One-line diagram
In power engineering, a one-line diagram or single-line diagram is a simplified notation for representing a three-phase power system. The one-line diagram has its largest application in power flow studies. Electrical elements such as circuit breakers, transformers, capacitors, bus bars, and...

, where only one phase is considered. However, due to the linear
Linear
In mathematics, a linear map or function f is a function which satisfies the following two properties:* Additivity : f = f + f...

ity of power systems, it is usual to consider the resulting voltage
Voltage
Voltage, otherwise known as electrical potential difference or electric tension is the difference in electric potential between two points — or the difference in electric potential energy per unit charge between two points...

s and currents as a superposition
Superposition
Superposition can refer to:* The superposition principle in physics, mathematics, and engineering, describes the overlapping of waves. Particular applications include :** Quantum superposition, in quantum physics** Superposition theorem, in electronics....

 of symmetrical components
Symmetrical components
In electrical engineering, the method of symmetrical components is used to simplify analysis of unbalanced three phase power systems under both normal and abnormal conditions.-Description:...

, to which three phase analysis can be applied.

In the method of symmetric components, the power system is seen as a superposition
Superposition theorem
The superposition theorem for electrical circuits states that the response in any branch of a bilateral linear circuit having more than one independent source equals the algebraic sum of the responses caused by each independent source acting alone, while all other independent sources are replaced...

 of three components:
  • a positive-sequence component, in which the phases are in the same order as the original system, i.e., a-b-c
  • a negative-sequence component, in which the phases are in the opposite order as the original system, i.e., a-c-b
  • a zero-sequence component, which is not truly a three phase system, but instead all three phases are in phase with each other.


To determine the currents resulting from an asymmetrical fault, one must first know the per-unit zero-, positive-, and negative-sequence impedances of the transmission lines, generators, and transformers involved. Three separate circuits are then constructed using these impedances. The individual circuits are then connected together in a particular arrangement that depends upon the type of fault being studied (this can be found in most power systems textbooks). Once the sequence circuits are properly connected, the network can then be analyzed using classical circuit analysis techniques. The solution results in voltages and currents that exist as symmetrical components; these must be transformed back into phase values by using the A matrix
Symmetrical components
In electrical engineering, the method of symmetrical components is used to simplify analysis of unbalanced three phase power systems under both normal and abnormal conditions.-Description:...

.

Analysis of the prospective short-circuit current is required for selection of protective devices such as fuses
Fuse (electrical)
In electronics and electrical engineering, a fuse is a type of low resistance resistor that acts as a sacrificial device to provide overcurrent protection, of either the load or source circuit...

 and circuit breaker
Circuit breaker
A circuit breaker is an automatically operated electrical switch designed to protect an electrical circuit from damage caused by overload or short circuit. Its basic function is to detect a fault condition and, by interrupting continuity, to immediately discontinue electrical flow...

s. If a circuit is to be properly protected, the fault current must be high enough to operate the protective device within as short a time as possible; also the protective device must be able to withstand the fault current and extinguish any resulting arcs without itself being destroyed or sustaining the arc for any significant length of time.

The magnitude of fault currents differ widely depending on the type of earthing system used, the installation's supply type and earthing system, and its proximity to the supply. For example, for a domestic UK 230 V, 60 A TN-S or USA 120 V/240 V supply, fault currents may be a few thousand amperes. Large low-voltage networks with multiple sources may have fault levels of 300,000 amperes. A high-resistance-grounded system may restrict line to ground fault current to only 5 amperes. Prior to selecting protective devices, prospective fault current must be measured reliably at the origin of the installation and at the furthest point of each circuit, and this information applied properly to the application of the circuits.

Detecting and locating faults

Locating faults in a cable system can be done either with the circuit de-energized, or in some cases, with the circuit under power. Fault location techniques can be broadly divided into terminal methods, which use voltages and currents measured at the ends of the cable, and tracer methods, which require inspection along the length of the cable. Terminal methods can be used to locate the general area of the fault, to expedite tracing on a long or buried cable.

In very simple wiring systems, the fault location is often found through visual inspection of the wires. In complex wiring systems (e.g. aircraft wiring) where the electrical wires may be hidden behind cabinets and extended for miles, wiring faults are located with a Time-domain reflectometer
Time-domain reflectometer
A time-domain reflectometer is an electronic instrument used to characterize and locate faults in metallic cables . It can also be used to locate discontinuities in a connector, printed circuit board, or any other electrical path...

. The time domain reflectometer sends a pulse down the wire and then analyzes the returning reflected pulse to identify faults within the electrical wire.

In historic submarine telegraph cables, sensitive galvanometer
Galvanometer
A galvanometer is a type of ammeter: an instrument for detecting and measuring electric current. It is an analog electromechanical transducer that produces a rotary deflection of some type of pointer in response to electric current flowing through its coil in a magnetic field. .Galvanometers were...

s were used to measure fault currents; by testing at both ends of a faulted cable, the fault location could be isolated to within a few miles, which allowed the cable to be grappled up and repaired. The Murray loop
Murray loop bridge
Murray loop bridge is a bridge circuit used for locating faults in underground or underwater cables. It has been used for more than 100 years....

and the Varley loop were two types of connections for locating faults in cables

Sometimes an insulation fault in a power cable will not show up at lower voltages. A "thumper" test set applies a high-energy, high-voltage pulse to the cable. Fault location is done by listening for the sound of the discharge at the fault. While this test contributes to damage at the cable site, it is practical because the faulted location would have to be re-insulated when found in any case.

In a high resistance grounded distribution system, a feeder may develop a fault to ground but the system continues in operation. The faulted, but energized, feeder can be found with a ring-type current transformer collecting all the phase wires of the circuit; only the circuit containing a fault to ground will show a net unbalanced current. To make the ground fault current easier to detect, the grounding resistor of the system may be switched between two values so that the fault current pulses.

Batteries

The prospective fault current of larger batteries, such as deep-cycle batteries
Deep cycle battery
A deep-cycle battery is a lead-acid battery designed to be regularly deeply discharged using most of its capacity. In contrast, starter batteries are designed to deliver short, high-current bursts for cranking the engine, thus frequently discharged of only a very small part of their capacity...

 used in stand-alone power system
Stand-alone power system
A stand-alone power system , also known as remote area power supply , is an off-the-grid electricity system for locations that are not fitted with an electricity distribution system...

s, is often given by the manufacturer.

In Australia, when this information is not given, the prospective fault current in amperes "should be considered to be 6 times the nominal battery capacity at the C A·h rate," according to AS 4086 part 2 (Appendix H).
The source of this article is wikipedia, the free encyclopedia.  The text of this article is licensed under the GFDL.
 
x
OK