A circuit breaker is an automatically-operated electrical
Electricity

Electricity is a general term that encompasses a variety of phenomena resulting from the presence and flow of electric charge. These include many easily recognizable phenomena such as lightning and static electricity, but in addition, less familiar concepts such as the electromagnetic field and electromagnetic induction....
 switch
Switch

In electronics, a switch is an electrical component which can break an electrical circuit, interrupting the Electric current or diverting it from one conductor to another....
 designed to protect an electrical circuit
Electrical network

An electrical network is an interconnection of electrical elements such as resistors, inductors, capacitors, transmission lines, voltage sources, current sources, and switches....
 from damage caused by overload
Overcurrent

In electricity supply, overcurrent or excess current is a situation where a larger than intended electric current exists through a conductor, leading to excessive generation of heat and the risk of damaging infrastructure and equipment and causing fires....
 or short circuit
Short circuit

A short circuit in an electrical circuit that allows a Electric current along a different path from the one intended.The electrical opposite of a short circuit is an "open circuit", which is an infinite resistance between two nodes....
. Its basic function is to detect a fault condition and, by interrupting continuity, to immediately discontinue electrical flow. Unlike a fuse
Fuse (electrical)

In electronics and electrical engineering a fuse is a type of overcurrent protection device. Its essential component is a metal wire or strip that melts when too much current flows, which breaks the electrical network in which it is connected, thus protecting the circuit's other components from damage due to excessive current....
, which operates once and then has to be replaced, a circuit breaker can be reset (either manually or automatically) to resume normal operation.






Discussion
Ask a question about 'Circuit breaker'
Start a new discussion about 'Circuit breaker'
Answer questions from other users
Full Discussion Forum



Recent Posts









Encyclopedia


Jtecul
A circuit breaker is an automatically-operated electrical
Electricity

Electricity is a general term that encompasses a variety of phenomena resulting from the presence and flow of electric charge. These include many easily recognizable phenomena such as lightning and static electricity, but in addition, less familiar concepts such as the electromagnetic field and electromagnetic induction....
 switch
Switch

In electronics, a switch is an electrical component which can break an electrical circuit, interrupting the Electric current or diverting it from one conductor to another....
 designed to protect an electrical circuit
Electrical network

An electrical network is an interconnection of electrical elements such as resistors, inductors, capacitors, transmission lines, voltage sources, current sources, and switches....
 from damage caused by overload
Overcurrent

In electricity supply, overcurrent or excess current is a situation where a larger than intended electric current exists through a conductor, leading to excessive generation of heat and the risk of damaging infrastructure and equipment and causing fires....
 or short circuit
Short circuit

A short circuit in an electrical circuit that allows a Electric current along a different path from the one intended.The electrical opposite of a short circuit is an "open circuit", which is an infinite resistance between two nodes....
. Its basic function is to detect a fault condition and, by interrupting continuity, to immediately discontinue electrical flow. Unlike a fuse
Fuse (electrical)

In electronics and electrical engineering a fuse is a type of overcurrent protection device. Its essential component is a metal wire or strip that melts when too much current flows, which breaks the electrical network in which it is connected, thus protecting the circuit's other components from damage due to excessive current....
, which operates once and then has to be replaced, a circuit breaker can be reset (either manually or automatically) to resume normal operation. Circuit breakers are made in varying sizes, from small devices that protect an individual household appliance up to large switchgear
Switchgear

The term switchgear, used in association with the electric power system, or grid, refers to the combination of electrical disconnects, Fuse and/or circuit breakers used to isolate electrical equipment....
 designed to protect high voltage circuits feeding an entire city.

Origins

An early form of circuit breaker was described by Edison
Thomas Edison

Thomas Alva Edison was an American inventor and businessman who developed many devices that greatly influenced life around the world, including the phonograph and the long-lasting, practical electric light bulb....
 in an 1879 patent application, although his commercial power distribution system used fuses
Fuse (electrical)

In electronics and electrical engineering a fuse is a type of overcurrent protection device. Its essential component is a metal wire or strip that melts when too much current flows, which breaks the electrical network in which it is connected, thus protecting the circuit's other components from damage due to excessive current....
. Its purpose was to protect lighting circuit wiring from accidental short-circuits and overloads.

Operation

All circuit breakers have common features in their operation, although details vary substantially depending on the voltage class, current rating and type of the circuit breaker.

The circuit breaker must detect a fault condition; in low-voltage circuit breakers this is usually done within the breaker enclosure. Circuit breakers for large currents or high voltages are usually arranged with pilot devices
Relay

A relay is an electrical switch that opens and closes under the control of another electrical circuit. In the original form, the switch is operated by an magnet to open or close one or many sets of contacts....
 to sense a fault current and to operate the trip opening mechanism. The trip solenoid
Solenoid

A solenoid is a three-dimensional coil. In physics, the term solenoid refers to a loop of wire, often wrapped around a metallic core, which produces a magnetic field when an electric current is passed through it....
 that releases the latch is usually energized by a separate battery, although some high-voltage circuit breakers are self-contained with current transformers, protection relays, and an internal control power source.

Once a fault is detected, contacts within the circuit breaker must open to interrupt the circuit; some mechanically-stored energy (using something such as springs or compressed air) contained within the breaker is used to separate the contacts, although some of the energy required may be obtained from the fault current itself. Small circuit breakers may be manually operated; larger units have solenoid
Solenoid

A solenoid is a three-dimensional coil. In physics, the term solenoid refers to a loop of wire, often wrapped around a metallic core, which produces a magnetic field when an electric current is passed through it....
s to trip the mechanism, and electric motors to restore energy to the springs.

The circuit breaker contacts must carry the load current without excessive heating, and must also withstand the heat of the arc produced when interrupting the circuit. Contacts are made of copper or copper alloys, silver alloys, and other materials. Service life of the contacts is limited by the erosion due to interrupting the arc. Miniature circuit breakers are usually discarded when the contacts are worn, but power circuit breakers and high-voltage circuit breakers have replaceable contacts.

When a current is interrupted, an arc
Electric arc

An electric arc is an electrical breakdown of a gas which produces an ongoing Plasma Electrostatic discharge, resulting from a current flowing through normally Electrical conductance media such as air....
 is generated - this arc must be contained, cooled, and extinguished in a controlled way, so that the gap between the contacts can again withstand the voltage in the circuit. Different circuit breakers use vacuum, air, insulating gas, or oil as the medium in which the arc forms. Different techniques are used to extinguish the arc including:
  • Lengthening of the arc
  • Intensive cooling (in jet chambers)
  • Division into partial arcs
  • Zero point quenching
  • Connecting capacitors in parallel with contacts in DC circuits


Finally, once the fault condition has been cleared, the contacts must again be closed to restore power to the interrupted circuit.

Arc interruption

Miniature low-voltage circuit breakers use air alone to extinguish the arc. Larger ratings will have metal plates or non-metallic arc chutes to divide and cool the arc. Magnetic blowout coils deflect the arc into the arc chute.

In larger ratings, oil circuit breakers rely upon vaporization of some of the oil to blast a jet of oil through the arc.

Gas (usually sulfur hexafluoride
Sulfur hexafluoride

Sulfur hexafluoride is an inorganic compound with the formula . It is a colorless, odorless, non-toxicity and non-flammable gas . has an octahedral geometry, consisting of six fluorine atoms attached to a central sulfur atom....
) circuit breakers sometimes stretch the arc using a magnetic field, and then rely upon the dielectric strength of the sulfur hexafluoride (SF6) to quench the stretched arc.

Vacuum circuit breakers have minimal arcing (as there is nothing to ionize other than the contact material), so the arc quenches when it is stretched a very small amount (<2-3 mm). Vacuum circuit breakers are frequently used in modern medium-voltage switchgear to 35,000 volts.

Air circuit breakers may use compressed air to blow out the arc, or alternatively, the contacts are rapidly swung into a small sealed chamber, the escaping of the displaced air thus blowing out the arc.

Circuit breakers are usually able to terminate all current very quickly: typically the arc is extinguished between 30 ms and 150 ms after the mechanism has been tripped, depending upon age and construction of the device.

Short circuit current


must incorporate various features to divide and extinguish the arc.

The maximum short-circuit current that a breaker can interrupt is determined by testing. Application of a breaker in a circuit with a prospective short-circuit current higher than the breaker's interrupting capacity rating may result in failure of the breaker to safely interrupt a fault. In a worst-case scenario the breaker may successfully interrupt the fault, only to explode when reset.

Miniature circuit breakers used to protect control circuits or small appliances may not have sufficient interrupting capacity to use at a panelboard; these circuit breakers are called "supplemental circuit protectors" to distinguish them from distribution-type circuit breakers.

Types of circuit breaker


Largecircuitbreaker
Many different classifications of circuit breakers can be made, based on their features such as voltage class, construction type, interrupting type, and structural features.

Low voltage circuit breakers

Circuitbreaker
Low voltage (less than 1000 VAC) types are common in domestic, commercial and industrial application, include:

  • MCB (Miniature Circuit Breaker)—rated current not more than 100 A. Trip characteristics normally not adjustable. Thermal or thermal-magnetic operation. Breakers illustrated above are in this category.


  • MCCB (Molded Case Circuit Breaker)—rated current up to 1000 A. Thermal or thermal-magnetic operation. Trip current may be adjustable in larger ratings.


  • Low voltage power circuit breakers can be mounted in multi-tiers in LV switchboards or switchgear
    Switchgear

    The term switchgear, used in association with the electric power system, or grid, refers to the combination of electrical disconnects, Fuse and/or circuit breakers used to isolate electrical equipment....
     cabinets.


The characteristics of LV circuit breakers are given by international standards such as IEC 947. These circuit breakers are often installed in draw-out enclosures that allow removal and interchange without dismantling the switchgear.

Large low-voltage molded case and power circuit breakers may have electrical motor operators, allowing them to be tripped (opened) and closed under remote control. These may form part of an automatic transfer switch system for standby power.

Low-voltage circuit breakers are also made for direct-current (DC) applications, for example DC supplied for subway lines. Special breakers are required for direct current because the arc does not have a natural tendency to go out on each half cycle as for alternating current. A direct current circuit breaker will have blow-out coils which generate a magnetic field that rapidly stretches the arc when interrupting direct current.

Small circuit breakers are either installed directly in equipment, or are arranged in a breaker panel.

The 10 ampere DIN rail
DIN rail

A DIN rail or top-hat rail is a standardized 35 mm wide metal rail with hat-shaped cross section. It is widely used, especially in Europe, for mounting circuit breakers and industrial control equipment inside equipment racks....
-mounted thermal-magnetic miniature circuit breaker is the most common style in modern domestic consumer unit
Consumer unit

A consumer unit is a box of fuse or circuit breaker, usually arranged in a single row. This is unlike a distribution board which has multiple rows of fuses or breakers and usually serves two or more locations, which may be split phase, two phase, two phases taken from three phase, or three phases....
s and commercial electrical distribution board
Distribution board

A distribution board is a component of an electricity supply system which divides an electrical power feed into subsidiary Circuit , while providing a protective Fuse or circuit breaker for each circuit, in a common Enclosure ....
s throughout Europe
Europe

Europe is, conventionally, one of the world's seven continents. Comprising the westernmost peninsula of Eurasia, Europe is generally divided from Asia to its east by the water divide of the Ural Mountains, the Ural , the Caspian Sea, and by the Caucasus Mountains to the southeast....
. The design includes the following components:

  1. Actuator lever
    Lever

    In physics, a lever is a rigid object that is used with an appropriate fulcrum or wiktionary:pivot point to multiply the mechanical force that can be applied to another object....
     - used to manually trip and reset the circuit breaker. Also indicates the status of the circuit breaker (On or Off/tripped). Most breakers are designed so they can still trip even if the lever is held or locked in the "on" position. This is sometimes referred to as "free trip" or "positive trip" operation.
  2. Actuator mechanism - forces the contacts together or apart.
  3. Contacts - Allow current when touching and break the current when moved apart.
  4. Terminals
  5. Bimetallic strip
  6. Calibration screw
    Screw

    A screw is a shaft with a helix groove or screw thread formed on its surface and provision at one end to turn the screw. Its main uses are as a threaded fastener used to hold objects together, and as a simple machine used to translate torque into linear force....
     - allows the manufacturer to precisely adjust the trip current of the device after assembly.
  7. Solenoid
  8. Arc divider / extinguisher


Magnetic circuit breaker

Magnetic circuit breakers use a solenoid
Solenoid

A solenoid is a three-dimensional coil. In physics, the term solenoid refers to a loop of wire, often wrapped around a metallic core, which produces a magnetic field when an electric current is passed through it....
 (electromagnet
Electromagnet

An electromagnet is a type of magnet in which the magnetic field is produced by the flow of electric Current . The magnetic field disappears when the current ceases....
) whose pulling force increases with the current. The circuit breaker contacts are held closed by a latch. As the current in the solenoid increases beyond the rating of the circuit breaker, the solenoid's pull releases the latch which then allows the contacts to open by spring action. Some types of magnetic breakers incorporate a hydraulic time delay feature using a viscous fluid. The core is restrained by a spring until the current exceeds the breaker rating. During an overload, the speed of the solenoid motion is restricted by the fluid. The delay permits brief current surges beyond normal running current for motor starting, energizing equipment, etc. Short circuit currents provide sufficient solenoid force to release the latch regardless of core position thus bypassing the delay feature. Ambient temperature affects the time delay but does not affect the current rating of a magnetic breaker.

Thermal magnetic circuit breaker


Thermal magnetic circuit breakers, which are the type found in most distribution board
Distribution board

A distribution board is a component of an electricity supply system which divides an electrical power feed into subsidiary Circuit , while providing a protective Fuse or circuit breaker for each circuit, in a common Enclosure ....
s, incorporate both techniques with the electromagnet responding instantaneously to large surges in current (short circuits) and the bimetallic strip responding to less extreme but longer-term over-current conditions.

Rated circuits

Circuit breakers are rated both by the normal current that are expected to carry, and the maximum short-circuit current that they can safely interrupt.

Under short-circuit conditions, a current many times greater than normal can exist (see maximum prospective short circuit current
Maximum prospective short circuit current

The prospective short circuit current is the highest Electric current which can exist in a particular electrical system under short circuit conditions....
). When electrical contacts open to interrupt a large current, there is a tendency for an arc
Electric arc

An electric arc is an electrical breakdown of a gas which produces an ongoing Plasma Electrostatic discharge, resulting from a current flowing through normally Electrical conductance media such as air....
 to form between the opened contacts, which would allow the current to continue. Therefore, circuit breakers must incorporate various features to divide and extinguish the arc. In air-insulated and miniature breakers an arc chute structure consisting (often) of metal plates or ceramic ridges cools the arc, and magnetic blowout coils deflect the arc into the arc chute. Larger circuit breakers such as those used in electrical power distribution may use vacuum
Vacuum

A vacuum is a volume of space that is essentially empty of matter, such that its gaseous pressure is much less than atmospheric pressure. The word comes from the Latin term for "empty," but in reality, no volume of space can ever be perfectly empty....
, an inert
Inert

In English, to be inert is to be in a state of doing little or nothing....
 gas
Gas

In physics, a gas is a state of matter, consisting of a collection of particles without a definite shape or volume that are in more or less random motion....
 such as sulphur hexafluoride or have contacts immersed in oil
Oil

An oil is a chemical substance that is in a viscosity liquid state at room temperature or slightly warmer, and is both hydrophobic and lipophilic ....
 to suppress the arc.

The maximum short-circuit current that a breaker can interrupt is determined by testing. Application of a breaker in a circuit with a prospective short-circuit current higher than the breaker's interrupting capacity rating may result in failure of the breaker to safely interrupt a fault. In a worst-case scenario the breaker may successfully interrupt the fault, only to explode when reset, injuring the technician.

International Standard
International standard

International standards are standards developed by international standards organisations. International standards are available for consideration and use, worldwide....
 IEC 60898-1 and European Standard EN 60898-1 define the rated current In of a circuit breaker for low voltage distribution applications as the current that the breaker is designed to carry continuously (at an ambient air temperature of 30 °C). The commonly-available preferred values for the rated current are 6 A, 10 A, 13 A, 16 A, 20 A, 25 A, 32 A, 40 A, 50 A, 63 A, 80 A and 100 A (Renard series, slightly modified to include current limit of British BS 1363
BS 1363

British Standard BS 1363 specifies the most common type of domestic AC power plugs and sockets that are used in the United Kingdom, Cyprus, Republic of Ireland, Malta, Malaysia, Singapore and many former British overseas territory....
 sockets). The circuit breaker is labeled with the rated current in ampere
Ampere

The ampere is the International System of Units unit of electric current. The ampere, in practice often shortened to amp, is an SI base unit, and is named after Andr?-Marie Amp?re, one of the main discoverers of electromagnetism....
, but without the unit symbol "A". Instead, the ampere figure is preceded by a letter "B", "C" or "D" that indicates the instantaneous tripping current, that is the minimum value of current that causes the circuit-breaker to trip without intentional time delay (i.e., in less than 100 ms), expressed in terms of In:
TypeInstantaneous tripping current
Babove 3 In up to and including 5 In
Cabove 5 In up to and including 10 In
Dabove 10 In up to and including 20 In
Kabove 8 In up to and including 12 In For the protection of loads that cause frequent short duration (approximately 400 ms to 2 s) current peaks in normal operation.
Zabove 2 In up to and including 3 In for periods in the order of tens of seconds. For the protection of loads such as semiconductor devices or measuring circuits using current transformers.


Common trip breakers


Breaker3phase2a Proc
When supplying a branch circuit with more than one live conductor, each live conductor must be protected by a breaker pole. To ensure that all live conductors are interrupted when any pole trips, a "common trip" breaker must be used. These may either contain two or three tripping mechanisms within one case, or for small breakers, may externally tie the poles together via their operating handles. Two pole common trip breakers are common on 120/240 volt systems where 240 volt loads (including major appliance
Major appliance

A major appliance, or domestic appliance, is usually defined as a large machine which accomplishes some routine housekeeping task, which includes purposes such as cooking, food preservation, or cleaning, whether in a household, institutional, commercial or industrial setting....
s or further distribution boards) span the two live wires. Three-pole common trip breakers are typically used to supply three-phase electric power
Three-phase electric power

Three-phase electric power is a common method of Alternating-current electric power electric power electric power transmission. It is a type of polyphase system, and is the most common method used by electric power distribution grids worldwide to distribute power....
 to large motors or further distribution boards.,

Medium-voltage circuit breakers


Medium-voltage circuit breakers rated between 1 and 72 kV may be assembled into metal-enclosed switchgear line ups for indoor use, or may be individual components installed outdoors in a substation
Substation

Substation can refer to:*Electrical substation*A police substation *The Substation, a Singaporean contemporary arts centre...
. Air-break circuit breakers replaced oil-filled units for indoor applications, but are now themselves being replaced by vacuum circuit breakers (up to about 35 kV). Like the high voltage circuit breakers described below, these are also operated by current sensing protective relay
Relay

A relay is an electrical switch that opens and closes under the control of another electrical circuit. In the original form, the switch is operated by an magnet to open or close one or many sets of contacts....
s operated through current transformer
Current transformer

In electrical engineering, a current transformer is used for measurement of electric currents. Current transformers are also known as instrument transformers....
s. The characteristics of MV breakers are given by international standards such as IEC 62271. Medium-voltage circuit breakers nearly always use separate current sensors and protection relays, instead of relying on built-in thermal or magnetic overcurrent sensors.

Medium-voltage circuit breakers can be classified by the medium used to extinguish the arc:

  • Vacuum circuit breaker—With rated current up to 3000 A, these breakers interrupt the current by creating and extinguishing the arc in a vacuum container. These are generally applied for voltages up to about 35,000 V, which corresponds roughly to the medium-voltage range of power systems. Vacuum circuit breakers tend to have longer life expectancies between overhaul than do air circuit breakers.


  • Air circuit breaker—Rated current up to 10,000 A. Trip characteristics are often fully adjustable including configurable trip thresholds and delays. Usually electronically controlled, though some models are microprocessor
    Microprocessor

    A microprocessor incorporates most or all of the functions of a central processing unit on a single integrated circuit . The first microprocessors emerged in the early 1970s and were used for electronic calculators, using Binary-coded decimal arithmetic on 4-bit Word ....
     controlled via an integral electronic trip unit. Often used for main power distribution in large industrial plant, where the breakers are arranged in draw-out enclosures for ease of maintenance.


  • SF6 circuit breakers extinguish the arc in a chamber filled with sulfur heaxafluoride gas.


Medium-voltage circuit breakers may be connected into the circuit by bolted connections to bus bars or wires, especially in outdoor switchyards. Medium-voltage circuit breakers in switchgear line-ups are often built with draw-out construction, allowing the breaker to be removed without disturbing the power circuit connections, using a motor-operated or hand-cranked mechanism to separate the breaker from its enclosure.

High-voltage circuit breakers

Electrical power transmission
Power transmission

Power transmission is the movement of energy from its place of generation to a location where it is applied to performing useful Mechanical work....
 networks are protected and controlled by high-voltage breakers. The definition of "high voltage" varies but in power transmission work is usually thought to be 72,500 V or higher, according to a recent definition by the International Electrotechnical Commission
International Electrotechnical Commission

The International Electrotechnical Commission is a Non-profit organization, non-governmental international standards organization that prepares and publishes International Standards for all electrical, electronic and related technologies ? collectively known as "electrotechnology"....
 (IEC). High-voltage breakers are nearly always solenoid
Solenoid

A solenoid is a three-dimensional coil. In physics, the term solenoid refers to a loop of wire, often wrapped around a metallic core, which produces a magnetic field when an electric current is passed through it....
-operated, with current sensing protective relay
Relay

A relay is an electrical switch that opens and closes under the control of another electrical circuit. In the original form, the switch is operated by an magnet to open or close one or many sets of contacts....
s operated through current transformer
Current transformer

In electrical engineering, a current transformer is used for measurement of electric currents. Current transformers are also known as instrument transformers....
s. In substation
Electrical substation

An electrical substation is a subsidiary station of an electricity Electrical generation, electric power transmission and electricity distribution system where voltage is transformed from high to low or the reverse using transformers....
s the protection relay
Relay

A relay is an electrical switch that opens and closes under the control of another electrical circuit. In the original form, the switch is operated by an magnet to open or close one or many sets of contacts....
 scheme can be complex, protecting equipment and busses from various types of overload or ground/earth fault.

High-voltage breakers are broadly classified by the medium used to extinguish the arc.
  • Bulk oil
  • Minimum oil
  • Air blast
  • SF6
    Sulfur hexafluoride

    Sulfur hexafluoride is an inorganic compound with the formula . It is a colorless, odorless, non-toxicity and non-flammable gas . has an octahedral geometry, consisting of six fluorine atoms attached to a central sulfur atom....
Some of the manufacturers are ABB
ABB

ABB is a three-letter abbreviation that may refer to:*ABB Grain Limited, an Australian agribusiness*ABB Group, formerly Asea Brown Boveri, a multinational corporation based in Switzerland...
, AREVA
Areva

AREVA is a Government-owned corporation multinational industrial Conglomerate that is mainly known for nuclear power; it also has interests in other energy projects....
, Mitsubishi Electric, Cutler-Hammer (Eaton
Eaton Corporation

Eaton Corporation is a diversified industrial manufacturer with 2008 sales of $15.4 billion . Eaton is a global leader in electrical systems and components for power quality, distribution and control; fluid power systems and services for industrial, mobile and aircraft equipment; intelligent truck drivetrain systems for safety and fuel econo...
), Siemens
Siemens

Siemens AG is a German electrical and telecommunications companysiemens may refer to*siemens , the SI unit of electrical conductance, equivalent to 1 ampere/volt...
, Toshiba
Toshiba

is a multinational corporation list of conglomerates manufacturing company, headquartered in Tokyo, Japan. The company's main business is in Infrastructure, Consumer Products, and Electronic devices and components....
, Schneider Electric
Schneider Electric

Schneider Electric is a France global company. It was founded in 1836 by two brothers, Eug?ne I and Adolphe Schneider.In the first part of the 20th century, Schneider et Cie associated itself with Westinghouse Electric Corporation who were a major international electrical group at the time....
 and others.

Circuit breaker can be classified as "live tank", where the enclosure that contains the breaking mechanism is at line potential, or dead tank with the enclosure at earth potential. High-voltage AC circuit breakers are routinely available with ratings up to 765,000 volts.

High-voltage circuit breakers used on transmission systems may be arranged to allow a single pole of a three-phase line to trip, instead of tripping all three poles; for some classes of faults this improves the system stability and availability.

Sulfur Hexafluoride (SF6) high-voltage circuit-breakers


High-voltage circuit-breakers have greatly changed since they were first introduced about 40 years ago, and several interrupting principles have been developed that have contributed successively to a large reduction of the operating energy. These breakers are available for indoor or outdoor applications, the latter being in the form of breaker poles housed in ceramic insulators mounted on a structure.

Current interruption in a high-voltage circuit-breaker is obtained by separating two contacts in a medium, such as SF6, having excellent dielectric and arc quenching properties. After contact separation, current is carried through an arc and is interrupted when this arc is cooled by a gas blast of sufficient intensity.

Gas blast applied on the arc must be able to cool it rapidly so that gas temperature between the contacts is reduced from 20,000 K to less than 2000 K in a few hundred microseconds, so that it is able to withstand the transient recovery voltage
Transient Recovery Voltage

A transient recovery voltage for high-voltage circuit breakers is the voltage that appears across the terminals after current interruption. It is a critical parameter for fault interruption by a high-voltage circuit breaker, its characteristics can lead either to a successful current interruption or to a failure ....
 that is applied across the contacts after current interruption. Sulphur hexafluoride is generally used in present high-voltage circuit-breakers (of rated voltage higher than 52 kV).

In the 1980s and 1990s, the pressure necessary to blast the arc was generated mostly by gas heating using arc energy. It is now possible to use low energy spring-loaded mechanisms to drive high-voltage circuit-breakers up to 800 kV.

Brief history

The first patents on the use of SF6 as an interrupting medium were filed in Germany in 1938 by Vitaly Grosse (AEG
AEG

AEG was a Germany producer of electronics and electrical equipment. AEG was founded in 1883 by Emil Rathenau who had bought some patents from American inventor Thomas Edison....
) and independently later in the USA in July 1951 by H.J. Lingal, T.E. Browne and A.P. Storm (Westinghouse). The first industrial application of SF6 for current interruption dates back to 1953. High-voltage 15 kV to 161 kV load switches were developed with a breaking capacity of 600 A. The first high-voltage SF6 circuit-breaker built in 1956 by Westinghouse, could interrupt 5 kA under 115 kV, but it had 6 interrupting chambers in series per pole. In 1957, the puffer-type technique was introduced for SF6 circuit breakers where the relative movement of a piston and a cylinder linked to the moving part is used to generate the pressure rise necessary to blast the arc via a nozzle made of insulating material (figure 1). In this technique, the pressure rise is obtained mainly by gas compression. The first high-voltage SF6 circuit-breaker with a high short-circuit current capability was produced by Westinghouse in 1959. This dead tank circuit-breaker could interrupt 41.8 kA under 138 kV (10,000 MV·A) and 37.6 kA under 230 kV (15,000 MV·A). This performance were already significant, but the three chambers per pole and the high pressure source needed for the blast (1.35 MPa) was a constraint that had to be avoided in subsequent developments. The excellent properties of SF6 lead to the fast extension of this technique in the 1970s and to its use for the development of circuit breakers with high interrupting capability, up to 800 kV.

Fig 1
The achievement around 1983 of the first single-break 245 kV and the corresponding 420kV to 550 kV and 800 kV, with respectively 2, 3, and 4 chambers per pole, lead to the dominance of SF6 circuit breakers in the complete range of high voltages.

Several characteristics of SF6 circuit breakers can explain their success:

  • Simplicity of the interrupting chamber which does not need an auxiliary breaking chamber;
  • Autonomy provided by the puffer technique;
  • The possibility to obtain the highest performance, up to 63 kA, with a reduced number of interrupting chambers;
  • Short break time of 2 to 2.5 cycles;
  • High electrical endurance, allowing at least 25 years of operation without reconditioning;
  • Possible compact solutions when used for "gas insulated switchgear" (GIS) or hybrid switchgear;
  • Integrated closing resistors or synchronized operations to reduce switching over-voltages;
  • Reliability and availability;
  • Low noise levels.


The reduction in the number of interrupting chambers per pole has led to a considerable simplification of circuit breakers as well as the number of parts and seals required. As a direct consequence, the reliability of circuit breakers improved, as verified later on by CIGRE surveys.

Thermal blast chambers

New types of SF6 breaking chambers, which implement innovative interrupting principles, have been developed over the past 15 years, with the objective of reducing the operating energy of the circuit-breaker. One aim of this evolution was to further increase the reliability by reducing the dynamic forces in the pole. Developments since 1996 have seen the use of the self-blast technique of interruption for SF6 interrupting chambers.

These developments have been facilitated by the progress made in digital simulations that were widely used to optimize the geometry of the interrupting chamber and the linkage between the poles and the mechanism.

This technique has proved to be very efficient and has been widely applied for high voltage circuit breakers up to 550 kV. It has allowed the development of new ranges of circuit breakers operated by low energy spring-operated mechanisms.

Thermal
The reduction of operating energy was mainly achieved by the lowering energy used for gas compression and by making increased use of arc energy to produce the pressure necessary to quench the arc and obtain current interruption. Low current interruption, up to about 30% of rated short-circuit current, is obtained by a puffer blast.

Self-blast chambers


Further development in the thermal blast technique was made by the introduction of a valve between the expansion and compression volumes. When interrupting low currents the valve opens under the effect of the overpressure generated in the compression volume. The blow-out of the arc is made as in a puffer circuit breaker thanks to the compression of the gas obtained by the piston action. In the case of high currents interruption, the arc energy produces a high overpressure in the expansion volume, which leads to the closure of the valve and thus isolating the expansion volume from the compression volume. The overpressure necessary for breaking is obtained by the optimal use of the thermal effect and of the nozzle clogging effect produced whenever the cross-section of the arc significantly reduces the exhaust of gas in the nozzle. In order to avoid excessive energy consumption by gas compression, a valve is fitted on the piston in order to limit the overpressure in the compression to a value necessary for the interruption of low short circuit currents.

Disjoncteur Selfblast
This technique, known as “self-blast” has now been used extensively since 1996 for the development of many types of interrupting chambers. The increased understanding of arc interruption obtained by digital simulations and validation through breaking tests, contribute to a higher reliability of these self-blast circuit breakers. In addition the reduction in operating energy, allowed by the self blast technique, leads to longer service life.

Double motion of contacts


An important decrease in operating energy can also be obtained by reducing the kinetic energy consumed during the tripping operation. One way is to displace the two arcing contacts in opposite directions so that the arc speed is half that of a conventional layout with a single mobile contact.

Disjoncteur Ht Fig5
The thermal and self blast principles have enabled the use of low energy spring mechanisms for the operation of high voltage circuit breakers. They progressively replaced the puffer technique in the 1980s; first in 72.5 kV breakers, and then from 145 kV to 800 kV.

Comparison of single motion and double motion techniques


The double motion technique halves the tripping speed of the moving part. In principle, the kinetic energy could be quartered if the total moving mass was not increased. However, as the total moving mass is increased, the practical reduction in kinetic energy is closer to 60%. The total tripping energy also includes the compression energy, which is almost the same for both techniques. Thus, the reduction of the total tripping energy is lower, about 30%, although the exact value depends on the application and the operating mechanism. Depending on the specific case, either the double motion or the single motion technique can be cheaper. Other considerations, such as rationalization of the circuit-breaker range, can also influence the cost.

Thermal blast chamber with arc-assisted opening


In this interruption principle arc energy is used, on the one hand to generate the blast by thermal expansion and, on the other hand, to accelerate the moving part of the circuit breaker when interrupting high currents. The overpressure produced by the arc energy downstream of the interruption zone is applied on an auxiliary piston linked with the moving part. The resulting force accelerates the moving part, thus increasing the energy available for tripping.

With this interrupting principle it is possible, during high-current interruptions, to increase by about 30% the tripping energy delivered by the operating mechanism and to maintain the opening speed independently of the current. It is obviously better suited to circuit-breakers with high breaking currents such as Generator circuit-breakers.

Generator circuit-breakers


Generator circuit-breakers are connected between a generator and the step-up voltage transformer. They are generally used at the outlet of high power generators (100 MVA to 1800 MVA) in order to protect them in a reliable, fast and economic manner. Such circuit breakers must be able to allow the passage of high permanent currents under continuous service (6.3 kA to 40 kA), and have a high breaking capacity (63 kA to 275 kA). They belong to the medium voltage range, but the TRV withstand capability required by ANSI/IEEE Standard C37.013 is such that the interrupting principles developed for the high-voltage range must be used. A particular embodiment of the thermal blast technique has been developed and applied to generator circuit-breakers. The self-blast technique described above is also widely used in SF6 generator circuit breakers, in which the contact system is driven by a low-energy, spring-operated mechanism. An example of such a device is shown in the figure below; this circuit breaker is rated for 17.5 kV and 63 kA.

Gcb

Evolution of tripping energy


The operating energy has been reduced by 5 to 7 times during this period of 27 years. This illustrates well the great progress made in this field of interrupting techniques for high-voltage circuit-breakers.

Future perspectives


In the near future, present interrupting technologies can be applied to circuit-breakers with the higher rated breaking currents (63 kA to 80 kA) required in some networks with increasing power generation.

Self blast or thermal blast circuit breakers are now accepted world wide and they have been in service for high voltage applications for about 15 years, starting with the voltage level of 72.5 kV. Today this technique is also available for the voltage levels 420/550/800 kV.

Other breakers


The following types are described in separate articles.
  • Breakers for protections against earth faults too small to trip an over-current device:
    • Residual-current device
      Residual-current device

      A residual current device , similar to that of a residual current circuit breaker , is an electrical wiring device that disconnects a circuit whenever it detects that the electric current is not balanced between the energized conductor and the return Ground and neutral conductor....
       (RCD, formerly known as a Residual Current Circuit Breaker) — detects current imbalance, but does not provide over-current protection.
    • Residual Current Breaker with Over-current protection
      Residual-current device

      A residual current device , similar to that of a residual current circuit breaker , is an electrical wiring device that disconnects a circuit whenever it detects that the electric current is not balanced between the energized conductor and the return Ground and neutral conductor....
       (RCBO) — combines the functions of an RCD and an MCB in one package. In the United States
      United States

      The United States of America is a Federal government constitutional republic comprising U.S. state and a federal district. The country is situated mostly in central North America, where its Contiguous United States and Washington, D.C., the Capital districts and territories, lie between the Pacific Ocean and Atlantic Oceans, Borders of the U...
       and Canada, panel-mounted devices that combine ground (earth) fault detection and over-current protection are called Ground Fault Circuit Interrupter (GFCI) breakers; a wall mounted outlet device providing ground fault detection only is called a GFI.
    • Earth leakage circuit breaker (ELCB) — This detects earth current directly rather than detecting imbalance. They are no longer seen in new installations for various reasons.


  • Autorecloser
    Autorecloser

    In electric power distribution, an autorecloser is a circuit breaker equipped with a mechanism that can automatically close the breaker after it has been opened due to a fault ....
     — A type of circuit breaker which closes again after a delay. These are used on overhead power distribution systems, to prevent short duration faults from causing sustained outages.


  • Polyswitch (polyfuse) — A small device commonly described as an automatically resetting fuse rather than a circuit breaker.


See also

  • Protective Device Coordination
    Protective Device Coordination

    Electrical Protective Device for distributed power systems consist of fuse , circuit breakers, relays and other types of devices typically designed to interrupt the current flow in an electrical power system....
  • Residual current device
  • Earth leakage circuit breaker
    Earth leakage circuit breaker

    File:ELCB_Panasonic_30A_type_2P2E.jpgAn Earth Leakage Circuit Breaker is a safety device used in electrical installations with high Earthing system to prevent shock....
  • Earthing system
    Earthing system

    In electricity supply systems, an Ground system defines the electrical potential of the conductors relative to that of the Earth's conductive surface....
  • Domestic AC power plugs and sockets
    Domestic AC power plugs and sockets

    AC power plugs and sockets are devices for removably connecting electrically-operated devices to the mains electricity.An electric plug is a gender of connectors and fasteners electrical connector with contact prongs to connect mechanically and electrically to slots in the matching female socket....
  • Arc-fault circuit interrupter
    Arc-fault circuit interrupter

    An arc fault circuit interrupter is a circuit breaker designed to prevent fires by detecting non-working spark and disconnect power before the arc starts a fire....
  • Insulation Monitoring Device
    Insulation monitoring device

    An insulation monitoring device monitors the Earthing system#IT network between an active phase conductor and Ground . It is intended to give an alert or disconect the power supply when the Electrical impedance between the two conductors drops below a set value, usually 50 kOhm....
  • Circuit Total Limitation (CTL)


External links

  • .